Modsoft ver. 2.62 1

Status
Not open for further replies.

tdob

Industrial
Apr 29, 2004
1
I'm using a modicon quantum PLC to control a cell and the software we must use is Modsoft ver. 2.62. I've found the manual 890USE115 and browsed through it. However I can't figure out how to force on an input or output any tips would be greatly appreciated also if you can direct me to where I can get any other sort of manuals (and yes i have already exhausted the schnieder website). Thanks for your time.
 
Replies continue below

Recommended for you

When you are in a network on a contact or coil you can hit the * key and force the contact from there. Are you can hold the alt-f2 key type the address you which to force. That will give the condition use the arrow key to move right change the E to D move bact to 0 or 1 and change it to however you want the input/output.

Hope this helps.

Mike
 