Mixing overcurrent devices

Status
Not open for further replies.

althomas49

Electrical
Mar 24, 2012
2
When selecting motor feeder circuit short circuit and ground fault protection, the code states:

You must provide the feeder with a protective device with a rating or setting not greater than the largest rating or setting of the branch-circuit short-circuit and ground-fault protective device (plus the sum of the full-load currents of the other motors of the group)

So if I use dual element time delay fuses for the branch circuits, but an inverse time breaker for the feeder, do I still use largest fuse rating for the calculation, or do I need to size the breaker as if the branch circuits were protected by inverse time breakers as well?
 
Replies continue below

Recommended for you

No, you recalculate the branch circuit protection as breakers and use that information to size the feeder protection.
430.62(A)says: "...based on the maximum permitted value for the specific type of a protective device in accordance with 430.52..."
 