Hello. I have a raised beam connection with a W12X30 end that bears on top of a W16X67 and then a W10x33 column below the W16. Similar to 13th Ed. AISC Manual Fig. 10-31(b). There is a minimal concentrated load of 15k acting on top of the W12. I do not think stiffeners are required for strength because the load is so low. However, I would like to provide full depth stiffeners for rotational stability of the W12 and W16. Rotational stability is required per specification section J and Appendix 6 according to my interpretation. What is the minimum stiffener required for stability? I was thinking of applying Appendix 6 (Stability Bracing for Columns and Beams). Assume a framed structure with W12 and W16 beams. Calculate the required nodal brace system stiffness. Then size the stiffener plate such that is has the same lateral stiffness.
I think the load is so low that it will not matter, but I would just like to know the proper way to do the design. I would guess that I will use a 3/8" full depth stiffener with 3/16" welds as a minimum.
Thenk you very much for any input you can provide!