Ran into an interesting conundrum. AISC Table 10-5 for unstiffened seated connections has you enter the table with a required bearing length, Nreq. Let's say you calculate a very small required bearing length for the loads you're taking with the connection. However, per AISC 360 J10.2 the minimum bearing length lb = not less than k for end beam reactions. So, if we have a large beam which has a large k value per Table 1-1 what do we enter Table 10-5 with? The minimum bearing length of k or the calculated minimum bearing length?
My thought was to use the calculated bearing length but wasn't sure if this would be 100% conservative.
Professional and Structural Engineer (ME, NH)
American Concrete Industries
My thought was to use the calculated bearing length but wasn't sure if this would be 100% conservative.
Professional and Structural Engineer (ME, NH)
American Concrete Industries