Hello JNCZA,
Don`t perform the test at 10 KV is better at 5 KV because you only needs to take an insulation reading.
The Recommended minimun Insulation resistances(IRmin)values corrected at 40 C as Defined by IEEE 43-2000 like:
"IR min= KV + 1 ,For most windings made before about 1970,all field windings"
"IRmin= 100 MOhm, for most DC armatures and AC Windings built after about 1970 (Form wound coils)"
Best Regards,
PETRONILA
A 500 V Megger is suitable for machines rated up to 2.4 KV above this this voltage a 1000 V Megger is recommended.