Medium Voltage Switchgears -33 kV- 2000A 31,5kA ( self power consumption)
mcm00048
21
Good Morning Colleages,
I have been looking through the forum but I have not found anything related.
I am wondering if anyone of you could tell me which is the approximated self power consumption of a MV Switchgear panel (Feeder for static load) of the features: 33kV , 2000 A and 31,5kA sc.Auxiliary voltage supply is 230 V AC and 110 V DC
I would need to make a rough calculation of it.
Thank you very much in advance and regards,
Miguel .
I typically see a 25 kVA station service transformer, though that seems to be much higher than actual demand. A few thoughts to get you started:
DC:
<25 Watts per relay/device
0.5-5 Watts per panel light
??? DC powered emergency lighting
??? trip/close coil & charging motors can be a large draw for a short time period.
AC:
100 Watts per compartment for anti-condensation heat
??? for switchgear HVAC depending on climate and size
??? overhead lighting inside the switchgear
??? Battery charger per DC load plus losses plus battery recharge rate