Meaning of CT 1200/5

Status
Not open for further replies.

ProtectiveBoy

Electrical
Sep 24, 2008
5
Hi,

When the current transformer is label 1200/5:
1. Is that means primary current that not exceed 1200A, the transformer will operate in linear region?
2.If the primary current more than 1200A, then the transformer operate in saturation region?
 
Replies continue below

Recommended for you

Hi ProtectiveBoy.
1200/5 is only transformation ratio.
Please see attached threads for the start.
thread238-208800
thread238-204485
thread238-217008 ( include great document of Shnaieder)
Best Regards and Good Luck.
Slava
 
You have to know the "rating factor" to know maximum continuous current. RF = multiple of rated current (ratio) that the CT can handle continuously without overheating. It's based on a given ambient, for instance in the US, it's generally based on a 30C average ambient over a 24 hr period.

RF also defines the upper limit of the metering accuracy class.

 