I have an application where digital outputs from a PLC will be required to operate a solenoid valve in the field - 800m away(i.e., a cable length of 1600m between the PLC DO terminals).
The solenoid valve is rated 24V DC, 12W and will work upto 22V DC.I want to use a 1.5mm2 copper cable (say), which has a resistance of 13.14 ohm/km. The digital output card is rated for 24V DC (say). Will the valve operate at all?
Or, do I have to use a higher interrogation voltage and solenoid valve of a higher voltage rating?
I know this is all a simple problem involving Ohm's Law - but, somehow, I am not sure.
Will someone comment?
The solenoid valve is rated 24V DC, 12W and will work upto 22V DC.I want to use a 1.5mm2 copper cable (say), which has a resistance of 13.14 ohm/km. The digital output card is rated for 24V DC (say). Will the valve operate at all?
Or, do I have to use a higher interrogation voltage and solenoid valve of a higher voltage rating?
I know this is all a simple problem involving Ohm's Law - but, somehow, I am not sure.
Will someone comment?