masonry stress

Status
Not open for further replies.

hello12345hello

Structural
Apr 25, 2011
50
I have new W-beam lintel sits on existing unreinforced masonry wall. reaction is 10 kip. What is allowable bearing stress for URM. Wall is 6in thick. Do i have to use same 0.25f'm.

 
Replies continue below

Recommended for you

Bearing on the full area of the wall, if it is special inspected, then the answer is yes.

If it is not specially inspected, then you are only allowed half that value. Sounds like you're in this range to me.

Mike McCann