cherryg222
We have a project in Mexico, where the client has insisted on ungrounded (delta-delta connection of Transformer) system for Low voltage (480V). From the design basis, it is clear that the purpose is to maintain power to process loads, which cannot be shut down without proper supervision and safety.
Now comes the fun stuff. We are also asked to supply HVAC loads from the same process MCC which is a part of the ungrounded system.
Now my question is: Does NEC (Article 250.21) allow ungrounded system for HVAC? Article 250.21 of NEC is pretty specific about ungrounded systems and where they are permitted.
Specifically, in my opinion, HVAC systems are far more susceptible to manual intervention. Many a times, even a nearby safety switch may not be operated to investigate a problem in a HVAC unit. If a L-G fault exists, and the person/persons touch the equipment, even though the system is ungrounded, leakage current in the tune of 1 to 2A per MVA can flow due to capacitive ground of several kms of lv cables. In my opinion, all non-process loads like HVAC should be supplied separately from solidly grounded system (separate Transformers + LV MCCs).
One more piece of info: Mexico country code is NOM-001-SEDE-2012 which is an adopted version of NEC.
Let me hear what is your opinion on this.