kmkassanju,
From the results I would say that, typical ratio for O2/N2 is 0.5 for in-service transformers.
Your oil indicates a ratio of 0.11,
If it is less than 0.3, it indicates,
1) The transformer is absorbing outside air through the conservator (not through the bladder)
or through possible leaks in sealed equipment.
2) Consuming too much O2 due to age & degradation of paper insulation
The O2 inhibitor mixed in oil "ABSORBS" the O2 in oil and keep the O2 content low in oil.
A time may come that the inhibitor is saturated and cannot "ABSORB" any more O2.
Therefore, my advise is,
(a) Verify the current inhibitor level in oil
(b) Verify the current acid number
by a lab test and compare with the spec for new oil or in-service oil.
Hope this helps.