McSEpllc
Structural
- Feb 25, 2006
- 108
Hi Everyone,
A concrete cylinder break was tested at 1,140 psi at 7 days for the footing of a retaining wall. This is below the roughly 1,575 psi compressive strength it should be. The design and specification are based on 3,000 psi. Swiss hammer tests confirmed the low concrete strength. The shear capacity of the heel of the footing is over-stressed for this condition, the toe is fine. The retaining wall is 19’-6” high and is supporting a pool on the upper level.
I am thinking about adding additional concrete on top of the footing and tying it with dowels for shear transfer and monolithical behavior. The GC already set the reinforcing and form for 60-ft of the wall in place.
My questions are:
- Has anyone done a repair like this before?
- Can the wall be placed before the footing extension? In theory only the heel would need strengthening, which could be doweled to the face of the wall. This goes against my gut-feel though.
- I presume I can find the amount of shear resisted by EI ratio of the existing and added footing. Is this how you would analyze this?
- A retarder had been added to the concrete mix as this was a pump mix. Could a retarder delay strength to this degree after 7 days? Does anyone have past experience on what percentage the strength would be at 7 days vs. 28 days using retarder?
Thanks!
Eric
Eric McDonald, PE
McDonald Structural Engineering, PLLC
A concrete cylinder break was tested at 1,140 psi at 7 days for the footing of a retaining wall. This is below the roughly 1,575 psi compressive strength it should be. The design and specification are based on 3,000 psi. Swiss hammer tests confirmed the low concrete strength. The shear capacity of the heel of the footing is over-stressed for this condition, the toe is fine. The retaining wall is 19’-6” high and is supporting a pool on the upper level.
I am thinking about adding additional concrete on top of the footing and tying it with dowels for shear transfer and monolithical behavior. The GC already set the reinforcing and form for 60-ft of the wall in place.
My questions are:
- Has anyone done a repair like this before?
- Can the wall be placed before the footing extension? In theory only the heel would need strengthening, which could be doweled to the face of the wall. This goes against my gut-feel though.
- I presume I can find the amount of shear resisted by EI ratio of the existing and added footing. Is this how you would analyze this?
- A retarder had been added to the concrete mix as this was a pump mix. Could a retarder delay strength to this degree after 7 days? Does anyone have past experience on what percentage the strength would be at 7 days vs. 28 days using retarder?
Thanks!
Eric
Eric McDonald, PE
McDonald Structural Engineering, PLLC