Recently a subcontractor of ours poured weather exposed concrete with a design strength of 5000psi and air content to be in conformance with Air limits as specified in ACI 301. 1 of the 4 pours came up super low with a corresponding air content of 9.0%. The 9% air concrete was noted in the field and was allowed to be poured (that's another story). Here are the 28 day break results and corresponding AC readings for the first 3 pours and 14 day for pour4:
Pour1- 5720psi, 6.8% Air
Pour2- 6435psi, 5.7% Air
Pour3- 2690psi, 9.0% Air
Pour4- 4715psi, 7.5% Air (14day)
Questions:
1.)Does pour 3 have any chance at gaining 85% f'c (4259)? (I think I know the answer to that one)
2.)If the results of the coring are within 85% f'c is this acceptable or is it purely up to the engineer of record to determine acceptance?
3.)Are there any other methods of testing in-situ concrete which I am missing?
I have dealt with this issue as an engineer now I'm on the contractor side (the dark side) and ripping this stuff out while possible, will be extremely costly
Thank you for any insight
Pour1- 5720psi, 6.8% Air
Pour2- 6435psi, 5.7% Air
Pour3- 2690psi, 9.0% Air
Pour4- 4715psi, 7.5% Air (14day)
Questions:
1.)Does pour 3 have any chance at gaining 85% f'c (4259)? (I think I know the answer to that one)
2.)If the results of the coring are within 85% f'c is this acceptable or is it purely up to the engineer of record to determine acceptance?
3.)Are there any other methods of testing in-situ concrete which I am missing?
I have dealt with this issue as an engineer now I'm on the contractor side (the dark side) and ripping this stuff out while possible, will be extremely costly
Thank you for any insight