Low Air Supervisory

Status
Not open for further replies.

ContractorDave

Mechanical
Joined
Jan 16, 2007
Messages
364
Location
CA
On a related note to an earlier posting, I do not see where it is mandatory to have low air supervision on a dry system. If it is a code requirement, then power to the air supply is in effect self monitoring. If it is not and a system exists without low air trouble, there exists ample room for error if a compressor is merely plugged into a receptacle.
Thoughts?

Regards
Dave
 
Low air supervision is not a requirement but an excellent, and fairly cheap, addition.

 
first you have to have a fire alarm panel installed to monitor the system, not always the case.
 
Technically required for refrigerated spaces only per NFPA 13 (2002 edition). However, we require them all on systems we specify/design:

7.8* Refrigerated Spaces.
7.8.2.2 Low Air Pressure Alarm.
7.8.2.2.1 Unless the requirements of 7.8.2.2.2 are met, a low air pressure alarm to a constantly attended location shall be installed.
7.8.2.2.2 Systems equipped with local low pressure alarms and an automatic air maintenance device shall not be required to alarm to a constantly attended location.
 