I have a couple questions about long-term composite steel beam deflections due to creep/shrinkage:

When is it necessary to consider them? Is there is a certain DL/LL ratio where it should be calculated?

Also, how do you account for the creep/shrinkage when you think it is necessary? I have read about people only considering half of the concrete modulus in deflection calculations.
 
SSEDTA 2001 Last modified 22/09/05

"Structural Steelwork Eurocodes Development of A Trans-national Approach"

See images in the attached zip. The last formula in the 3d image points to 67% effective stiffness of concrete (respect full effective section considered).

Effective width can be taken 100% when for slabs under uniform loads.

More complete engineering judgement tips can be extolled from the reference.


 
 http://files.engineering.com/getfile.aspx?folder=d2af6b35-7783-403b-9809-8cac2350a785&file=Composite_Beams_Deflection_EC4.zip
In the same reference I quoted above ...

"In practical floor construction, these requirements are met (although not explicitly
stated in EC4) if the span:depth ratio of the composite section is less than the
following:
• for simply supported beams: 15 to 18 for main beams, 18 to 20 for
secondary beams (joists);
• for continuous beams: 18 to 22 for main beams, 22 to 25 for secondary
beams (joists)."
 