The answer depends on the spacing of the supporting beams underneath and the amount of slab overhanging on each side of the two exterior beams (assuming there are more than two to begin with). Most bridge slabs are design looking at two cases 1. the overhang forces/moments and 2. the section of slab between the beams for both positive and negative moment. If the overhang or the interior negative moment controls the design then the rebar required by design will be placed near the top of the slab. The remaining rebar is for load distribution, temperature and serviceability.
While this is most likely a private application, most bridge deck slabs are 8.5" with the minimum being 7.5. Thus you should give some thought to increasing the slab thickness. The smaller slab will result in larger rebar, which, in turn, will result in serviceability problems and placement problems.
The spacing of the reinforcing would be controlled by the design.
For more information, please contact your local building enforcement official. They can be very helpful and provide some insight so that the constructed product doesn't fall apart only a few months later.