You’ve left out building type, building age, occupancy, if sprinkled, and combustibles present. But under normal conditions, the FACP should be located within or along the designated entrance corridor or lobby, as approved by AHJ. Area in front of FACP should remain clear of obstructions. Remote Anunciators may be required by AHJ, where multiple entrances exist. If you are concerned with voltage drop issues, nominal supplemental power extenders can be remote of FACP for lengthy applications to alarm notification appliances.