Hi TD2K,
Thanks for your input. We design the vessel (fuel gas scrubber) with a liquid trap/auto drainer on the liquid line instead of putting LCV with on/off operation based on the liquid level inside the vessel. This is because the liquid drop off from the gas stream is fairly small in the vessel. The recovered liquid from the vessel we route it to Closed Drain Vessel which is also acts as LP Flare Knock-out drum. We size the vessel to cater for 7 MMSCFD gas max and 420 blpd max. These two flowrates is not coincident. The maximum gas going to the scrubber is 5 MMSCFD. The design pressure of the closed drain vessel is 7 barg and the max OP of the fuel gas scrubber is 5.2 barg. Hence i believe the gas blowby scenario occured in the fuel gas scrubber can be handled by the downstream equipment, i.e piping and closed drian vessel (LP Flare KO drum).
And thinking back, since the liquid drop off is fairly minimal, how do I set the set point of the LSLL because the minimum liquid amount will varies and i might experience frequent unit tripping of the vessel which will of course disturb the process flow.