Hi Mates!
I would like to know your opinion on lightning protection on areas where zone 1 and 2 are classified.
I met design that all parts of LPS are outside hazardous zones.
It is reasonable.
However the att D5.1 of IEC 62395-3 says that 1m separation is needed, but if it is impossible and conductors passing the hazardous zone, they shall be continuous, or connection amount shall be minimized.
Further -connections shall be secure (brazing, welding, clamping, crimping, seaming, screwing, bolting).
In effect - it is ordinary lightning protection.
What is in NFPA?
I reviewed NFPA 780 and nothing found about any limitation.
Do you have any experience with that?
Thanks