NFPA 780 requirement:
6.2.2 Corrosion Protection. Copper and bronze materials
used on the upper 7.6 m (25 ft) of a stack shall have a continuous
covering of lead having minimum thickness of 1.6 mm
(1⁄16 in.) to resist corrosion by flue gases
6.3.5.1 An electrically continuous steel hood covering the
stack lining and column, having a metal thickness of not less
than 4.8 mm (3⁄16 in.), shall be permitted to serve as the strike
termination device.
However, if the hood it is of stainless steel made the maximum continuously applied temperature it has to be not more than 450 oC.
You may try the NASA copper alloy GRCop-84: A High-Temperature Copper Alloy for High-Heat-Flux Applications. This material withstands maximum 800oC.