PRPA
Mechanical
- Apr 27, 2010
- 7
Quick bit of background. I volunteer at the local curling club, helping out with the ice and ice equipment. We run an Ammonia-Brine system and four years ago built new supply and return headers for the brine distribution. The original equipment, circa 1960 was all steel, but we replaced it will PVC as it is more resistant to brine running through it.
The setup is pretty simple. The supply and return headers are both an 80' length of 4" SCH80 PVC that has been drilled and tapped every 6" along the length. Each of those holes has 1" hose barb cemented into it. The system worked great the first couple of years, however this year we noticed brine starting to disappear from the make-up tank. After some investigation, we've found that four of these hose barbs have developed leaks that need to be fixed.
The problem is that correcting the problem with hose barbs that have been cemented is not so easy. Cutting/drilling out the old one requires the brine from the whole system to be drained and refilled once the job is complete. That's a major undertaking for a small group of volunteers.
This is where I'm looking for some advice/input from fellow engineers. Since the leaks are all very small and system is fairly low pressure (20-22psi), is there another solution? Like building up some epoxy around the hose barb connection? I'm thinking about a product like "JB-Weld Waterweld" or some similar putty type epoxy. Does anyone have experience with these products, especially in regards to being used in an environment where it would be exposed to cold conditions, ice build up and contact with brine?
Any input would be greatly appreciated.
The setup is pretty simple. The supply and return headers are both an 80' length of 4" SCH80 PVC that has been drilled and tapped every 6" along the length. Each of those holes has 1" hose barb cemented into it. The system worked great the first couple of years, however this year we noticed brine starting to disappear from the make-up tank. After some investigation, we've found that four of these hose barbs have developed leaks that need to be fixed.
The problem is that correcting the problem with hose barbs that have been cemented is not so easy. Cutting/drilling out the old one requires the brine from the whole system to be drained and refilled once the job is complete. That's a major undertaking for a small group of volunteers.
This is where I'm looking for some advice/input from fellow engineers. Since the leaks are all very small and system is fairly low pressure (20-22psi), is there another solution? Like building up some epoxy around the hose barb connection? I'm thinking about a product like "JB-Weld Waterweld" or some similar putty type epoxy. Does anyone have experience with these products, especially in regards to being used in an environment where it would be exposed to cold conditions, ice build up and contact with brine?
Any input would be greatly appreciated.