Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Leak Detection of Petroleum Double-Wall Tank

Status
Not open for further replies.

davster01

Industrial
Nov 12, 2006
16
Hi,

There seems to be many methods of continuously monitoring an aboveground double-wall tanks for leaks. We were thinking of using a Veeder-Root TLS 350 for both piping and the tanks.

These are a couple of 10 000 liters tanks feeding a power generator that is running continuously.

The question I have is what is the best way (lowest maintenance) for monitoring the tanks? Should I look at the pressure in the interstitial space, or at the presence of hydrocarbon in the interstitial space or at the variation of liquid volumes inside the primary tank (hydrocarbon and water).

Thank you
davster01
 
Replies continue below

Recommended for you

I thought double wall tanks all came with float switches in the interstitial space.



Mike Halloran
Pembroke Pines, FL, USA
 
Hi Davster01,

I also suggest you look at the new OPW iSite,

The iSite gives you various options for monitoring the interstitial spaces.

In my opinion, the lowest maintenance unit would be a duel hydrocarbon/water sensor.

Please visit

Over Pressure Protection; Flow, Level & Density Measurement; Automation and Control.
Electronic Presets; Additive Systems.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor