Hello SS7
If the supply is too weak to start this machine DOL, you can use a reduced voltage starter (of which there are a number of options) provided that the motor is capable of generating sufficient shaft torque at the reduced starting current.
As the start voltage is reduced, (independent of starter type) the start torque will reduce by the square of the current reduction. i.e. at half voltage, you will have half current and a quarter of the torque.
With large machines, the typical starting torque is much lower than with small machines. The starting torque is a function of rotor design, and with a machine of this size ist must be a custom build and so a high start torque rotor should be specified.
The driven load determines the minimum starting torque required. The driven load should be looked at to see if there is any opportunity to reduce the start torque requirement, for example, a screw compressor can be pressure equalized during start, a pump can be started against a closed valve etc.
The motor determines the conversion from Amps start current into NM torque and the starter controls the actual current supplied.
If the load requires a high start torque and this can not be reduced, then a secondary resistance starter and motor may be required.
The big mistake that many people make is to ignore the motor starting characteristics when making the purchase, and then being faced with a less than ideal situation when reduced starting current is required.
If you can provide more information, I am sure that there is some good engineering advice available here.
Best regards,
Mark Empson