timm333

Electrical
Jun 4, 2009
121
If we put a terminal block in an enclosure, for example universal-enclosure of Schneider, then do we need to consider the short circuit rating of only of the terminal blocks, or short circuit rating of enclosures as well?
 
Replies continue below

Recommended for you

I don't know what could be the short-circuit withstand test of a junction box.UL-50 indicate a "pressure test" and could be sufficient for usually low-voltage short-circuit arc flash in a junction box. Of course if the employee opens the box cover he has to be equipped as per NFPA 70E:
"Standard for Electrical Safety in the Workplace". According to NEC the non energized metallic parts have to be grounded [see Art.250-122].The requirement for short-circuit test is for boxes containing fuses or breakers as switchgear or MCC and other.
 
Thanks 7anoter4. Another question comes to mind.

Why is it that the arc flash study is required for 480V MCC/switchgear, but is not required for a 480V panelboard?

 