Joint Efficiency for Large Storage Tanks

Status
Not open for further replies.

mecharya

Mechanical
Joined
Aug 9, 2008
Messages
3
Location
CA
Hello,

As per Section 6 of API 650, it seems for large storage tanks joint efficiency is not considered 1.00(notations of Figure 6-1 mentioned spot radiography). Is it right?

What shall we use as joint efficiency in E.6.2.4(b) for large storage tanks? (tanks which not included in Appendix A)

Thank you in advance

Arya
 
API-650 assumes a 100% joint efficiency for the standard design. This does not require full radiography except in heavier plate, and should not be confused with the requirements of ASME. (Note that allowable stresses are a lot different from ASME as well.)

Under App. A, you can use reduced or omitted radiography with lower joint efficiencies.
 
Thank you for your help JStephen. :-)

 