moiz19670309
Mechanical
- Jun 15, 2013
- 30
Hello'
NFPA 20 requires the head at 150% flow to be atleast 65% of rated head. It also requires the head at 0% flow to be no more than 140% of rated head.
Being client some one is installing Fire Protection System in our plant. We have witnessed the Pump tests. During the jockey pump test, its maximum pressure at 0 flow came out to be 172%. We have objected about this increase from limiting 140% to 172%. But the Fire Protection System designer says that he will install a pressure relief valve at the discharge of jockey pump and hence limit the 172% to 140%. He says NFPA allows it for pressure maintaining devices.
Is he right or should we reject the pump.
Kindly help me.
Moiz Khan
NFPA 20 requires the head at 150% flow to be atleast 65% of rated head. It also requires the head at 0% flow to be no more than 140% of rated head.
Being client some one is installing Fire Protection System in our plant. We have witnessed the Pump tests. During the jockey pump test, its maximum pressure at 0 flow came out to be 172%. We have objected about this increase from limiting 140% to 172%. But the Fire Protection System designer says that he will install a pressure relief valve at the discharge of jockey pump and hence limit the 172% to 140%. He says NFPA allows it for pressure maintaining devices.