rpruitt
Specifier/Regulator
- Apr 16, 2003
- 1
I am of the belief that an isolated ground bus should be connected to the system with an insulated ground wire to the point where the earth ground wire from the ground rod connects to the service entrance ground/neutral. I was told it is just fine to just make this connection inside the building at the neutral bus of the main panel. The IG panel is a sub-panel two feet from the main panel making the IG bus connection only 30” long then connected to the main panel neutral lug bonding all together. I do not see where this accomplishes anything at all. It is the same as running the branch circuits (IG’s) to the main panel instead and making their connections at that point. The current flowing flowing in the grounded conductor (neutral) between the panelboard and separately derived system (transformer) would cause instability (noise) in the ground reference. I am having a little trouble understanding exactly what the NEC is directing on this. I read it as the connection should be at the service entrance but I am being overridden. This system is 208v 3 phase and the building has more than one occupancy (separate metering). Can someone clarify this for me?