Nov 8, 2002 #1 DavT Electrical Joined Nov 8, 2002 Messages 3 Location GB Can any one advise what the power used by a Hitachi L300P 22kW/30HP inverter would be when powered up but in Standby mode, I have looked through the Hitachi manual and can see no figures given, does any one have any ideas ?
Can any one advise what the power used by a Hitachi L300P 22kW/30HP inverter would be when powered up but in Standby mode, I have looked through the Hitachi manual and can see no figures given, does any one have any ideas ?
Nov 8, 2002 #2 cbarn24050 Industrial Joined Jan 20, 2002 Messages 709 Location GB Hi, nothing significant just a few watts to run the internal electronics. Upvote 0 Downvote
Nov 9, 2002 #3 jbartos Electrical Joined Jan 15, 2000 Messages 6,440 Suggestion: Check the efficiency figure. Then, the idle kW will be (1-EFF) x Input kW. Upvote 0 Downvote