- Oct 21, 2002
- 40
I have a problem regarding one client who ordered inverter and motor from different manufacturers and not matching characteristics. The inverter is for 315kW/ 3x400V, 50Hz asynchronous motor but the current capability (616A) and kVA rating are under what the supplied electric motor needs. It is an electric motor with 315kW but with cos PHI = 0.7 (rated speed 500rev/min, rated current 698A). They think to compensate the motor by adding a three phase capacitor in paralel at its terminals, but there is a problem with the inverter, it will not work (the distorted voltage of inverter, the inverter cannot have a capacitive load). I'm thinking to make a kind of filter by calculating an output reactor for the inverter and adding the capacitor in paralel to the motor. Which should be the resonant frequency of such filter? 50Hz ? Probably I would need to make a simulation?
Thanks for any clue.
Pafi