Interlocking logic

Status
Not open for further replies.

Mbrooke

Electrical
Joined
Nov 12, 2012
Messages
2,546
Location
US
When doing electrical interlocks for breakers, MODs, ground switches and other devices would you go with separate auxiliary relays or wire everything into the back of the Electronic Device (421/487E/451 relay) using freeform logic and boolean as interlocking?

What are the pros and cons of each?
 
For safety reasons, I would use a key or wired type interlock. And not a software interlock.

Too many people out their that can do logic faster than they can think.
 
Interesting perspective! I thought the other way around but you make a really good point.
 
I don't like software interlocks for anything tied to protection. I think it is bad practice and doesn't tie in well to company lock out tag out procedures. How do you tag a software interlock? No one has to physically interpret logic with a lockout relay with a tag or padlock. When people's safety is in mind, make everything as simple as allowable.
 
Never stopped to consider that aspect. Again, thank you! :)
 