Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations 3DDave on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Interior Load Bearing Wall Sole Plate Anchorage

Status
Not open for further replies.

NFExp

Structural
Jun 18, 2009
79
I would like to generate a discussion on sole plate anchorage for interior load bearing wood frame walls that are not shearwalls and have no uplift.

IRC R403.1.6.1 requires anchor bolts @ 6'-0" o.c. for seismic C & D. Does anyone know why?

For residential project, we usually specify 16d Masonry cut nails at 16" o.c. Does this seem reasonable? What does everyone else specify?

Keep in-mind I'm refering to light frame residential projects.

Thanks

 
Replies continue below

Recommended for you

The 6' bolt spacing is for out-of-plane loading for seismic or 5 psf minimum lateral loading on interior walls.

I prefer the Hilti X-U shot pin (16" spacing or so) in lieu of cut nails. These are easier to install, and you get a better connection.
 
I agree with Hokie. If the lateral values for the Hilti work, fine use them. But something is needed.

Also consider the fact that in a seismic event, the walls you describe can literally "walk" unless anchored somehow. And with time, and considering the actual method of construction in the field, some "non-bearing" walls become actual bearing walls over time.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
Check the shear from the 5psf interior lateral load and set accordingly. I prefer shot pins over cut nails.
 
Thanks for your responses.

I'm having some trouble with the building officals. They will only allow anchor bolts. I know that the IRC is perscriptive so I'll have to convince them that the cut nails or shot pins are acceptable.
 
I've found that a quick analysis and a sealed letter stating that my version is equivalent or better to the capacity of the prescriptive is usually enough to calm down the building department.
 