It is ususally not appropriate to test smpsu and filters at 500 v, because as already advised it can cause damage, and would also fail the test. Other circuits such as the power save mode on some computer monitors use a bridge of 4 x 330 ohm resistors which will return a value of 0.3 to 0.4 Mohm form a tied line neutral to earth test.
It is more reasonable to skip the insulation resistance test and perform a functional earth leakage measurement. This value (U.K) should be less than 3.5 miliamps.
Regards,
KVKEV