Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Inspection of a concrete slab on grade post pour

Status
Not open for further replies.

JEB777

Civil/Environmental
Sep 16, 2011
8
Is there a document online that will ref. ACI standards relating to inspection of a concrete slab after the pour. In other words, from an ACI standpoint, what should I be looking for as I examine a cured concrete slab on grade-in order to determine if the slab meets the ACI minimum standards?

thanks,
Joel
 
Replies continue below

Recommended for you

You could take a look at ACI 302.1R - Guide for Concrete Floor and Slab Construction. We have this manual in our office. Not sure if it is available online.

Also, ACI 117 gives guidelines for tolerances...
 
Flatness... maybe future curling or something
Uniformity of colour...
Cracking... type and location... may be future...
Sawcutting: spacing, depth, width, and timing
Curing... maybe future surfacing
Filling sawcut joints

There may be a few others...