Inline measurement of glycol in water

Status
Not open for further replies.

kinderli

Chemical
Joined
Sep 20, 2000
Messages
1
Location
GR
Dear All

We need to measure the inline consentration of glycol in water. The pipe size is 6" and the avg consentration is 30%. The temperature is 45 deg. C and 90 deg. C.
We need a 4-20 mA output and 24 vdc power supply.

Thank you for your help


Penelope Kinderli
Chemicai Engineer/Greece [sig][/sig]
 
The density of glycol and water are quite different and so a simple process density measurement will give you very good concentration measurement. A good densitometer will even include the temperature density referral to find the density at a reference temp for the solution from which to calculate the concentration. Glycol water data is well publicised on the web so setting up the system is relatively easy.
For a 6" line your best bet is an insertion density meter which installs in the side of the pipe and measures at your process conditions and gives you the results as %concentration.
You can search the web for density meters, densitometers, vibrational density meters etc or visit our web page.
Solartron Mobrey
 