We have a styrene storage tank that gets both pumped into and out of for polystyrene production. The tank is inerted with 0.5 psi of a nitrogen blanket. It looks like the blanketing system has malfunctioned during a shutdown. So we might have a situation for running with the blanketing system off. Concerns of mine are:
- don't know if there is a dip tube in the tank to help prevent static from free falling liquid.
- any codes that state that styrene needs inerted (even during colder months)
Does anyone have a method using temperature to see if the vapor space in the tank will reach above the LEL of styrene? I think I remember it has to do with vapor pressure of styrene at the certain conditions and has to correlate with LEL?
Also any other concrens I have to look at?
Thanks.