Hello all -
Would like to know your thoughts on the following problem.
Putting it as concisely as possible, a chiller plant was replaced with a larger one. The condenser water system, however, re-used the old 6-inch piping to and from the cooling tower due to the cost of digging up piping and replacing it with 8" or 10". There's about 400 feet of pipe with a few turns and the velocity is high (~11 feet per second at design flow). The condenser pump suction, which is about 20 feet below the cooling tower sump (about 400 feet in x, -20 feet in y), reads about 16 inches of mercury below atmosphere when operating. The air separator even operates at a vacuum so (I believe) it does not have a way to expell the air it separates. The system periodically shows evidence of vapor binding and pump cavitation.
The best solution would obviously be to replace the piping. The cheapest solution I envision is a bladder type expansion tank piped into the top of the air separator, or at some other point on the pump suction line, near the pump. This would be located some 400 feet of pipe downstream of the cooling tower sump, and yes, in an open system. IS THIS REASONABLE? The thought is that some amount of NPSH would be added during operation, allowing the air separator to remove air while increasing the NPSH. When the system is shut down, the bladder should contract (or expand and push up the sump level?), but the sump volume rise or fall would be limited by the bladder size.
Is there a conceptual error with applying this to an open system? Has anyone applied a bladder tank in a similar instance to resolve such a problem?
Thanks in advance for any help with this. -CB
Would like to know your thoughts on the following problem.
Putting it as concisely as possible, a chiller plant was replaced with a larger one. The condenser water system, however, re-used the old 6-inch piping to and from the cooling tower due to the cost of digging up piping and replacing it with 8" or 10". There's about 400 feet of pipe with a few turns and the velocity is high (~11 feet per second at design flow). The condenser pump suction, which is about 20 feet below the cooling tower sump (about 400 feet in x, -20 feet in y), reads about 16 inches of mercury below atmosphere when operating. The air separator even operates at a vacuum so (I believe) it does not have a way to expell the air it separates. The system periodically shows evidence of vapor binding and pump cavitation.
The best solution would obviously be to replace the piping. The cheapest solution I envision is a bladder type expansion tank piped into the top of the air separator, or at some other point on the pump suction line, near the pump. This would be located some 400 feet of pipe downstream of the cooling tower sump, and yes, in an open system. IS THIS REASONABLE? The thought is that some amount of NPSH would be added during operation, allowing the air separator to remove air while increasing the NPSH. When the system is shut down, the bladder should contract (or expand and push up the sump level?), but the sump volume rise or fall would be limited by the bladder size.
Is there a conceptual error with applying this to an open system? Has anyone applied a bladder tank in a similar instance to resolve such a problem?
Thanks in advance for any help with this. -CB