I understand that the nitrogen consumption for blanketing system of tank can be calculated as the method in API 2000. In consideration of “in-breathing” flow rate, the total requirement is the sume of following two scenarios.
a.) The resultant flow in to the tank due to the out-flow of liquid during emptying.
b.) Thermal in-breathing due to the atmospheric cooling effect (contracting or condensing) on the vapor within the tank.

My question is about the basis of thermal in-breathing in API Standard 2000. The inbreathing rate can be found in the table which is increased with tank capacity. If the tank has insulation and heating coil, the temperature change will be less than 100 F/hr in the vapor space. Please advise me how to calculate the nitrogen consumption in this case.
 
The inbreathing rates calculations in API 2000 are described in one of the appendices in the back. They were essentially calculated based on an unisulated tank being exposed to a sudden rain shower. Tests were done to estimate how much roof and shell plates could be cooled and that number was translated to a heat transfer to the gases inside the tank and then the amount of inbreathing requried to compensate for the skrinkage of those gases.

There's no cookbook how to do it for an insulated tank in API 2000. Obviously, the inbreathing rates will be far, far less due to the insulation. Where you are venting gases to the atmosphere or inbreathing ambient air, it's just not a factor in many cases since breather valves are relatively inexpensive and the savings from detailed engineering calculations for justifying an 8" versus a 10" using the flow rates out of AOI 2000 isn't likely worthwhile.

I understand your position. API 2000 when you are talking about a nitrogen system results in very high short term flows. I'd likely start with the cooling basis of the shell and roof plates in API 2000 but applied to the insulation covering of your tank and calculate a replacement volume for heat transfer across the insulation. Keep your air inbreathing/vent valves on the tank since your N2 supply is likely not guaranteed that you want to depend on it 100%. If it works properly, your atmospheric vent valves will never have to operate. Setting all your pressures and over/under pressures to get your requied flows for various cases will take some time and hopefully you have a reasonable design pressure/vacuum rating on the tank to work with.
 