camanu18,
USCS: Like BigH, I prefer to use more descriptive classifications for soils rather than just symbols. The US Army Corps of Engineers explains their (fairly standard) terms in Appendix F of their publication EM-1110-1-1804. It's good stuff - check it out at
.
Concrete Block: What you describe in your last post seems to me to be an anchor block for a guyed monopole. The fact that it's suporting a pole (not a pile) is not particularly relevant to the analysis of the block. What is important is knowing what maximum (design) vertical force will be exerted on the block by the guy cable.
The conservative design approach will likely assume that the sole resistance to vertical load is provided by the self-weight of the anchor block, unless the design code explcitly permits side resistance to be included. I would also imagine that if the design code permits side resistance, then it would also offer guidance on how to model the resistance.
However, as a mental excercise, we can look at possible approaches to determining the long-term side resistance.
Long-term, after the backfill has had time to settle around the block, we can look at the adhesion (in a cohesive soil) or friction (in a cohesionless soil) on the sides of the block and assume that there is no wedge displacement of the surrounding soil to simplify the idea and still stay fairly conservative.
I would think that an approach similar to that for the design of drilled shafts would be more appropriate than the approach for driven piles.
I would probably use a value of skin resistance of 0.7*0.55*su (see FHWA IF-99-025 "Drilled Shafts - Construction Procedures and Design Methods", pp.280, 288) for cohesive soil surrounding the block.
For cohesionless soils, the uplift resistance formulae for drilled shafts are dependent on the soil type and are given on pages 281 and 288, with further discussion in Appendix B.
Alternatively, it could be argued that the correct approach would be to look at the adhesion/friction force determination for backfilled rigid retaining walls. There are many texts on the subject (the NAVFAC manuals cover this subject, and the Canadian Foundation Engineering Manual also covers the subject fairly well), so I see no reason to tread over this ground again.
Note: Take care to check that the tendency of the block to overturn about the corner nearest the top of the tower has an adequate factor of safety. Also, depending on the backfill conditions, it may be prudent to assume that the near-surface backfill material will yield.
Hope this gives you some ideas,
Jeff
Jeffrey T. Donville, PE
TTL Associates, Inc.