e57
Electrical
- Feb 27, 2005
- 4
Hi all, new to your forums here. I'm an Electrician, not an Engineer, but have a possible engineering question.
I'm dealing with a customer (on a second opinion basis) that has a rather extreme "Rattle" of the conductors in an elevator feed. I noticed it when working on a TI in the building on the second floor! The elevator feed in the basement will rattle like a short on start-up, (really loud) to the point that it can be heard through-out the building. When I first heard it I went all over the building trying to locate it. Its a sound that says "trouble" when heard by an Electrician. After finding out that it was the elevator, I notified the Owner who says they have had nothing but trouble from this elevator. Replacing starters, occasionaly trips contactor, etc. And it turns out the Elevator Rep. and Electrician who installed the feed have been in several arguements about why this is happening. Elevator Rep suggested that the feed was not properly "tri-plexed" (Twisted on install) Ah... good point, but no-one does it, especially in runs this long. (140' through several turns) Then suggested that one could "Dampen" the noise by "Opening the conduit at the couplings, and fill it with expanding foam" This of course sent the Electrician into a rage. (Sent me into fits of laughter)
The Electrician who installed the feed, (250MCM) megged it out OK, and suggested that the 6 pole motor is mis-wired. Which I believe could be an issue, as it does have slightly differend amperage values pole to pole, but is wired OK.
I feel the differing pole to pole values may be due to damage to the motor, via Voltage Drop at Locked Rotor. However the LRA is slightly higher than Manufactures data, but not significant. Its a 200VAC 45HP 3phase 6 pole on a 208VAC system. VD on start-up is at 182. (which I see as borderline exessive, but possibly bad for extended life of the motor, which smells like its on its whay out) In rush amperage is hard to capture without proper PQM equipment, but varies from 650-700A, operating amperage levels out at 185A, 175A, 187A.
So now there are several suggestions for eleiminating this situation.
#1 Replacing feed with "Tri-plexed 4/0 feeder" Smaller than whats there... Or installing step up tranformer at begining, and step down at end of feed. (Via Elevator Rep)
#2 Replace 250MCM feed with 350MCM (Via Electrician who oringinally installed the feeder)
Then theres my opinion... Power Quality Monitoring before anything to get a clearer picture, and possibly replace motor with simular torque and speed but lower LRA via a 208/230 motor, but may take some shopping around to find a match.
So what do you guys think?
I'm dealing with a customer (on a second opinion basis) that has a rather extreme "Rattle" of the conductors in an elevator feed. I noticed it when working on a TI in the building on the second floor! The elevator feed in the basement will rattle like a short on start-up, (really loud) to the point that it can be heard through-out the building. When I first heard it I went all over the building trying to locate it. Its a sound that says "trouble" when heard by an Electrician. After finding out that it was the elevator, I notified the Owner who says they have had nothing but trouble from this elevator. Replacing starters, occasionaly trips contactor, etc. And it turns out the Elevator Rep. and Electrician who installed the feed have been in several arguements about why this is happening. Elevator Rep suggested that the feed was not properly "tri-plexed" (Twisted on install) Ah... good point, but no-one does it, especially in runs this long. (140' through several turns) Then suggested that one could "Dampen" the noise by "Opening the conduit at the couplings, and fill it with expanding foam" This of course sent the Electrician into a rage. (Sent me into fits of laughter)
The Electrician who installed the feed, (250MCM) megged it out OK, and suggested that the 6 pole motor is mis-wired. Which I believe could be an issue, as it does have slightly differend amperage values pole to pole, but is wired OK.
I feel the differing pole to pole values may be due to damage to the motor, via Voltage Drop at Locked Rotor. However the LRA is slightly higher than Manufactures data, but not significant. Its a 200VAC 45HP 3phase 6 pole on a 208VAC system. VD on start-up is at 182. (which I see as borderline exessive, but possibly bad for extended life of the motor, which smells like its on its whay out) In rush amperage is hard to capture without proper PQM equipment, but varies from 650-700A, operating amperage levels out at 185A, 175A, 187A.
So now there are several suggestions for eleiminating this situation.
#1 Replacing feed with "Tri-plexed 4/0 feeder" Smaller than whats there... Or installing step up tranformer at begining, and step down at end of feed. (Via Elevator Rep)
#2 Replace 250MCM feed with 350MCM (Via Electrician who oringinally installed the feeder)
Then theres my opinion... Power Quality Monitoring before anything to get a clearer picture, and possibly replace motor with simular torque and speed but lower LRA via a 208/230 motor, but may take some shopping around to find a match.
So what do you guys think?