I am looking to ask our protection people to revised some of the protection scheme currently employed by our utility. The scheme used currently is the fuse saving scheme. To improve MAIFI I am looking to employ the fuse blowing scheme on some feeders. What is the impact if any of this scheme on live line work. Is there any utility experiences where this is concern?
Off the bat one can argue that when the recloser is in the non-auto reclose mode to facilitate live line work if there is any mis-hap then the recloser will operate instantaneously on the fuse saving scheme than against a time delayed operation on the fuse blowing scheme. I believe that this is some what of a pseudo-protection. Any comment?
Off the bat one can argue that when the recloser is in the non-auto reclose mode to facilitate live line work if there is any mis-hap then the recloser will operate instantaneously on the fuse saving scheme than against a time delayed operation on the fuse blowing scheme. I believe that this is some what of a pseudo-protection. Any comment?