Nov 7, 2003 #1 anevarez Electrical Joined Nov 7, 2003 Messages 1 Location US Can an ignition transformer be used inside an enclosure bearing a UL508 label?
Nov 7, 2003 #2 buzzp Electrical Joined Nov 21, 2001 Messages 2,032 Location US The approval of the panel to 508 means it is a complete panel. When you add or remove components, the panel should be requalified. It does not matter if the component is UL recognized or listed. Check with AHJ and see what he says. Upvote 0 Downvote
The approval of the panel to 508 means it is a complete panel. When you add or remove components, the panel should be requalified. It does not matter if the component is UL recognized or listed. Check with AHJ and see what he says.