RSChinn
Electrical
- Nov 19, 2007
- 38
IEEE80(-2000)page 78, third and fourth paragraphs: "For a grounded Y on the secondary (distribution) side of a substation transformer, ground faults at the transformer low-side terminals circulate through the grid with negligible leakage current to the earth and thus no effect on the substation's GPR. However, for distribution (or low-side) faults a remote distance away a large portion of the fault current will return to the transformer neutral via the substation grid, thus contributing to the GPR." Q1: Does that last sentence mean a small (and no longer neglibible) current now flows in the soil and will create a GPR that is no longer insignificant? Q2: By using the high side fault current values to calculate GPR, we will not need to worry about the remote low side GPR since the high-side always will be bigger (provided there are no other low-side sources or transformers connected in parallel)?