Accordiong to the B16.5, flanges are not required to be hydrotested as part of the manufacturing process. However flanged fittings are not exempt. Is there a specific reason ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
2.6 System Hydrostatic Testing
Flanged joints and flanged fittings may be subjected
to system hydrostatic tests at a pressure of 1.5 times the
38°C (100°F) rating rounded off to the next higher 1 bar
(25 psi) increment. Testing at any higher pressure is
the responsibility of the user, taking into account the
requirements of the applicable code or regulation.
8 PRESSURE TESTING
8.1 Flange Test
Flanges are not required to be pressure tested.
8.2 Flanged Fitting Test
8.2.1 Shell Pressure Test. Each flanged fitting shall
be given a shell pressure test.
8.2.2 Test Conditions. The shell pressure test for
flanged fittings shall be at a pressure no less than 1.5
times the 38°C (100°F) pressure rating rounded off to
the next higher 1 bar (25 psi) increment.
8.2.3 Test Fluid. The pressure test shall be made
using water, which may contain a corrosion inhibitor or
kerosene as the test fluid. Other suitable test fluids may
be used provided their viscosity is no greater than that
of water. The test fluid temperature shall not exceed
50°C (125°F).
8.2.4 Test Duration. The test duration shall be as
follows:
Fitting Size Duration, sec
NPS ≤2 60
21⁄2 ≤ NPS ≤ 8 120
NPS ≥ 10 180
8.2.5 Acceptance. No visible leakage is permitted
through the pressure boundary wall.