Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Hydropheumatic tank sizing

Status
Not open for further replies.

ncsuboy

Civil/Environmental
Mar 2, 2010
2
NC admin code give an example of sizing a hydro tank as peak demand - pumping capacity x 20 min = required effective volume
so if i have (60-30)x20=600 gallons
then they state the total volume if you use a 60-40psi pressure cycle with automatic air water volume controls is required effective volume/0.25. So 2400 gallons
I assume this is based on Boyle's Law. What affect and how do you calculate the volume with precharging? How does this work. With no control the percentage of water would be 7% of the total volume on a 60-40 pressure cycle. so 8570 gallons in my example. Big difference. School me please.
 
Replies continue below

Recommended for you

Very usefull, thanks for the information.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor