May 28, 2012 #1 Archiekin Petroleum Joined Dec 5, 2007 Messages 2 Location CA If water is not available for hydrotesting a shop fabricated tank (Size: 23'-6" OD x 32' tall), instead the tank will be air/soap leak tested. Is this considered a modification to API 650 specs. or does that still comply API 650?
If water is not available for hydrotesting a shop fabricated tank (Size: 23'-6" OD x 32' tall), instead the tank will be air/soap leak tested. Is this considered a modification to API 650 specs. or does that still comply API 650?
May 29, 2012 1 #2 fegenbush Mechanical Joined Apr 5, 2006 Messages 783 Location US 7.3.5(2) or J.4.2.2 cover testing the shell in a manner other than hydrostatically with water. Air/soap is permitted in both sections. Upvote 0 Downvote
7.3.5(2) or J.4.2.2 cover testing the shell in a manner other than hydrostatically with water. Air/soap is permitted in both sections.
May 30, 2012 Thread starter #3 Archiekin Petroleum Joined Dec 5, 2007 Messages 2 Location CA Thanks fegenbush. Upvote 0 Downvote