Eng-Tips is the largest forum for Engineering Professionals on the Internet.

Members share and learn making Eng-Tips Forums the best source of engineering information on the Internet!

  • Congratulations dmapguru on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

HVAC problem 1

Status
Not open for further replies.

falcon1654

Mechanical
Joined
Sep 29, 2006
Messages
4
Location
CA
I am involved in designing a very small hvac system with a Blower Fan at 700 CFM 2inwg. I can not find a sutible equation that will give me the preassure losses for the following:

A 700 CFM supply entering a 15" diameter cone diverging to a 8" diameter circular duct. The cone is 17" long with an angle of 10 degs.

B. A circular spilter duct to split the 700 cfm to 350 cfm to different directions.
If anyone have any Ideas Falcon1654 would appreciate it.
 
The loss coefficient in your case for the area ratio of 3.51 (=15*15/8*8) with 100 taper is about 2.56. The velocity at inlet condition is about 570 fpm. Now calculate velocity pressure at inlet condition and multiply it with the loss coefficient. This gives you pressure loss at the section.

Refer to ASHRAE duct fitting database or SMACNA manual for other data.

 