P1ENG
Structural
- Aug 25, 2010
- 237
I have a 5.5" wide by 5/8" thick TRANSVERSE plate welded to an HSS8x8x3/8, because I am creating a W-flange beam to HSS moment connection.
Per equation K4-4, my calculated effective weld is 3.42" even though there will be 11" of weld (5.5" across top and bottom of plate). Based on my load and this effective length, I need a 1/2" fillet weld. This seems like a lot for a 3/8" thick wall tube. The last paragraph in section K4 (before the User Note) says:
"The weld checks in Table K4.1 are not required if the welds are capable of developing the full strength of the branch member wall along its entire perimeter (or a plate along its entire length)."
I think this will let me reduce my weld size, but I need help deciphering this statement. I don't understand what "developing the full strength" means. If my weld strength is equal to my plate's base metal strength, I don't need to calculate le per K4-4? Is "full strength" nominal or LRFD/ASD?
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant
Per equation K4-4, my calculated effective weld is 3.42" even though there will be 11" of weld (5.5" across top and bottom of plate). Based on my load and this effective length, I need a 1/2" fillet weld. This seems like a lot for a 3/8" thick wall tube. The last paragraph in section K4 (before the User Note) says:
"The weld checks in Table K4.1 are not required if the welds are capable of developing the full strength of the branch member wall along its entire perimeter (or a plate along its entire length)."
I think this will let me reduce my weld size, but I need help deciphering this statement. I don't understand what "developing the full strength" means. If my weld strength is equal to my plate's base metal strength, I don't need to calculate le per K4-4? Is "full strength" nominal or LRFD/ASD?
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant