I'm writing an RFP for a replacement stoplog lifting machine on a dam. I don't have to spec everything out in detail, but I am describing the machine operation required. I want to spec out a few key points to make sure we have some quality control over the final product.
The existing motor is a 20 HP 3 phase working from a 60 Amp supply of 250 VDC / 600 VAC power on the dam deck. The motor probably dates from the 1950s and the nameplate reads as follows:
GE Electric Motor 20 HP Phase 3 MR 404
55581-20-840-64-220-100
1/2HR 55 - 93.5 - 442359
I will leave the horsepower sizing up to the designer of the new machine, but suspect I want to call for the new motor to be TEFC enclosure (because of outdoor use). I figure manually-reset thermal overload protection is most appropriate. The machine may be abused so I want to call for a service factor of 1.15 But after that, I have questions.
Duty Cycle: At most, the machine operates for a few hours at a time, but the motor would see it as bursts of 5-7 minutes, break for a couple, another burst, and so on, for about a 4 hour stretch. Does this count as "Continuous Duty"?
We will likely have this thing for another 50 yrs so I'm looking at NEMA Premium Efficiency motors. But since the use pattern of use is start-stop-start-stop, would such a fancy motor be worth spending the extra money? Doesn't that efficiency stuff apply only to truly steady-state continuous use?
Load: Getting a log moving in the sluiceway involves friction of the log ends against the check under water pressure and current. This is higher as you go deeper or water is faster, so it varies. Similarly, when you place a log you want to go slower as you get to the bottom so you don't jam the machine. I can see some variation of torque with speed, does this mean I need a "constant horsepower" motor? Do you spec this out for the motor, or is it part of the way the controller is configured?
And speaking of controllers, is it enough to just describe the operation we want for the machine and say to the designer: "select VSD to suit?" Or do I need to keep reading and figure out how to spec one up better.
Sorry for the vagueness of the questions. Electrical stuff is quite new to me.
The existing motor is a 20 HP 3 phase working from a 60 Amp supply of 250 VDC / 600 VAC power on the dam deck. The motor probably dates from the 1950s and the nameplate reads as follows:
GE Electric Motor 20 HP Phase 3 MR 404
55581-20-840-64-220-100
1/2HR 55 - 93.5 - 442359
I will leave the horsepower sizing up to the designer of the new machine, but suspect I want to call for the new motor to be TEFC enclosure (because of outdoor use). I figure manually-reset thermal overload protection is most appropriate. The machine may be abused so I want to call for a service factor of 1.15 But after that, I have questions.
Duty Cycle: At most, the machine operates for a few hours at a time, but the motor would see it as bursts of 5-7 minutes, break for a couple, another burst, and so on, for about a 4 hour stretch. Does this count as "Continuous Duty"?
We will likely have this thing for another 50 yrs so I'm looking at NEMA Premium Efficiency motors. But since the use pattern of use is start-stop-start-stop, would such a fancy motor be worth spending the extra money? Doesn't that efficiency stuff apply only to truly steady-state continuous use?
Load: Getting a log moving in the sluiceway involves friction of the log ends against the check under water pressure and current. This is higher as you go deeper or water is faster, so it varies. Similarly, when you place a log you want to go slower as you get to the bottom so you don't jam the machine. I can see some variation of torque with speed, does this mean I need a "constant horsepower" motor? Do you spec this out for the motor, or is it part of the way the controller is configured?
And speaking of controllers, is it enough to just describe the operation we want for the machine and say to the designer: "select VSD to suit?" Or do I need to keep reading and figure out how to spec one up better.
Sorry for the vagueness of the questions. Electrical stuff is quite new to me.