Does the graph meet the manufacturing requirements ... i.e. temperature between 70-80oF and humidity 50%rh.
Looking at the trend of the graph the control appears to be relatively coarse, with no fine control. It appears almost on/off control with no modulation.
Also if the AHU is controlled on a return air probe close to the ahu, using air drawn from multiple rooms, are the other room conditions affecting the supply you need in the manufacturing room.
If the condition in the room need to be tightly controlled either change AHU control to the return from that room or install a local DX heating/cooling a/c unit to acheive fine control. Be aware tho that you could end up the a/c unit fighting the supply air from the AHU.