How does PMG reduce EMI/RFI?

Status
Not open for further replies.

jdub4

Electrical
Nov 10, 2009
3
A client of ours wants to specify a PMG on a ~55kW genset for the purposes of EMI reduction. How does this work?
I'm aware of the major benefit to PMG excitation as a reduction in the variations due to motor starting voltage drop, line harmonics, etc.
I can see that some manufacturers list EMI reduction as a benefit to PMG excitation, but details are lacking.
Can anyone enlighten me please?

Thanks for your help.
 
Replies continue below

Recommended for you

That's a new on me on me also. I will be eagerly awaiting an explanation.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
There is usually some HF commutation noise from the excitation system rectifier which can be detected at the main terminals of a bus-fed exciter. A PMG isolates the excitation system from the main output. I can't think of any normal generator application where this would be a problem except maybe broadcast or telecoms, and even then it would be unlikely.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Thanks Scotty.
Yours
Bill

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Many thanks.

Sounds like I'll have to figure out what they're really looking for, or afraid of.
 